| 1 | initial version |
In raw data bus I is the "Winding 1" bus and bus J is the "Winding 2" bus. Winding 1 is the winding where the tap changer is located. So, the first bus number (I) is always Winding 1 bus in raw data.
In PSSE the transformers are sorted with the lowest bus number as "From Bus" and the other as "To Bus". Here the location of the tap changer (at Winding 1) is defined by the check box "Winding 1 on From end". If I > J, then J becomes "From bus" and I becomes "To bus".