When machines with missing generator models are gnetted automatically at initialisation Pgen is modelled as constant current load and Qgen is modelled as contant impedance load. Both Pload and Qload are zero!
In the example below I have deleted the generator model for machine at bus 102 in savnw network. After initialisation, the machine is gnetted and replaced with a load:
The load data are shown below: