First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
1 | initial version |
Hey I think the issue you're seeing is due to how percent loading is calcualted on transformer vs. non-transformer branches. Transformers are by default on MVA loading whereas non-transformer are current expressed as MVA loading (assumes nominal voltage). Look in the Program Operation Manual for more on this, specifically ACCC and RATE. ACCC reports the line end with the larger loading.