First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!

Ask Your Question

Revision history [back]

click to hide/show revision 1
initial version

answered Aug 16 '1

perolofl gravatar image

As I understand it you are measuring the voltage at bus 5 and want to control the voltage at bus 1000.

Select RefFlag = 1 and VCFlag = 1. Rc and Xc shall be the impedance of the line (in pu system base) between bus 5 and bus 1000. Note, Kc is not used here.