Ask Your Question

Revision history [back]

click to hide/show revision 1
initial version

From purely utilitarian view point this is how I understand it:

Reactive current exceeds type of error messages mean that you have dynamic limits in dyr/snp set to lower than what the system gets as the initial values from the power flow calculation.

Solving this issue usually means changing the Usched in the power flow solution to force the generator close to 0 reactive power or changing the limits on the dynamic side. Naturally changing the model will affect how it performs, but this is in my understanding what causes these issues.