Xsource is usually set at a very large value e.g. 9999 p.u. However, please note that manufacturer's data of inverter shall be consulted before doing the modeling work. They typically provide modeling procedure of inverter for PSS/E steady-state and dynamic studies. An Aspen Oneliner modeling note is also given for short-circuit studies as well.