First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!

Ask Your Question

Revision history [back]

click to hide/show revision 1
initial version

answered Sep 9 '0

jfconroy gravatar image

As you say, the governor response is usually relatively slow, so it won't affect fault ride-through results significantly. However, if you are studying the frequency stability of a power system, then you should not turn off the governors.