First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
| 1 | initial version |
PSS/E picks current injection of bus to solve the equation. So either CURNT(Modeled as other types) or ISORCE(Modeled as Generator) array need to be taken care by your own. Please note that those arrays are both complex type. There is an example available in POM. Please refer "Writing a Basic Load Model" chapter. The ISORCE is similar with CRUNT, however, you also need consider ZSORCE affection.
whit loves you. Content on this site is licensed under a Creative Commons Attribution Share Alike 3.0 license.