These models don't need additional configution to be linked to the machine. In the dynamics data you indicate the bus and machine. If you want to change Power, in the REPCA model Fflag has to be 1 and you can modify VAR(L+), note it is in pu (/MVAmachine). For Q, ICON RefFlaf must be and VAR(L+1) is in pu too.

P and Q will be the machine ones if you do not monitored any Branch or the power through a line if you monitored one (ICONs M+1, M+2 and M+3)