1 | initial version |
Solutions in dynamics are usually in a case-by-case scenario. If you can, provide more info about your test. Check my post "flat run for pv plant" for some hints.
2 | No.2 Revision |
Solutions to issues in dynamics dynamic runs are usually in a case-by-case scenario. If you can, provide more info about your test.
test.
Check my post "flat run for pv plant" for some hints.
Check always the scale of your plots. After running a PSSe dynamic study, you can use PSSPLT to find the worst channels deviations using the idv file attached below. For deviation of Q channels, its is good to get 10E-02 or lower values: Sample from a flat start using savnw.sav:
CHANEL IDENTIFIER INITIAL VALUE DEVIATION TIME (SECONDS)
15 VARS 206[URBGEN 18.000]1 6.000 0.7153E-05 5.7375
16 VARS 211[HYDRO_G 20.000]1 0.1774 -0.4411E-05 9.1874
PSSPLT IDV file to get the max deviation of channels (adjust path an filenames):
MENU,OFF /* FORCE MENU TO CORRECT STATUS
PDEV
2,1,1
LOGs\SAVNW_wind_flat.err
ODEV
2,1,1
LOGs\SAVNW_wind_flat.err
text,* *************************************
text,* PLOT SAVNW_wind
text,*
text,* *************************************
CHNF
OUTs\SAVNW_wind_flat.out
RANG
1
SCAN
2 0 1
SAVNW_wind_MaxDevs.txt
4
1 2500
ANGL
20
1 2500
POWR
20
1 2500
VARS
20
1 2500
ETRM
20
STOP