First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
| 1 | initial version |
Check the internet for "plant model validation", also the following NERC presentation. The acceptable way to satisfy NERC Standards MOD 025-2,026-1,027-1, is to show that measurements recorded matched pretty well with simulation results. This presentation gives an introduction to the tests preformed.
The PSSe playback model PLBVFU1 allows to compare measurement against simulation output. Also, V-profiles or Freq-profiles can be set in the model to check simulated plant's models response. Check the post "Example using PLBVFU1 playback generator" for additional info.
| 2 | No.2 Revision |
Check the internet for "plant model validation", also the following NERC presentation. The acceptable way to satisfy NERC Standards MOD 025-2,026-1,027-1, is to show that measurements recorded matched pretty well with simulation results. This presentation gives an introduction to the tests preformed.
The PSSe playback model PLBVFU1 allows to compare measurement against simulation output. Also, V-profiles or Freq-profiles can be set in the model to check simulated plant's models response. Check the post "Example using PLBVFU1 playback generator" for additional info.
Check this forum for "PV and WTG Step Change". Yunzhi's tool DMview allows the simulation of multiple test (V, F, SCR)