The code flow is good. I re-arranged it, set it for one case run, runtime to 5 sec for testing and added a log file as well as change the integration step back to 1/4 of a cycle, recommended for more power system studies. This version run OK in v.33:
# -- coding:utf-8 --
import os,sys
import glob
PYTHONPATH = r'C:\Program Files (x86)\PTI\PSSE33\PSSBIN'
sys.path.append(PYTHONPATH)
os.environ['PATH'] += ';' + PYTHONPATH
import redirect
import psspy
psspy.psseinit(12000)
_i, _f = psspy.getbatdefaults()
#Redirect output from PSSE to Python:
redirect.psse2py()
GENERATORS = [[30,'1'],[31,'1'],[32,'1'],[33,'1'],[34,'1'],[35,'1'],[36,'1'],[37,'1'],[38,'1'],[39,'1']]
#Loop through cases
#for CASEi in glob.glob(os.path.join('C:\Users\Desktop\IEEE39_new\sav\', '*.sav')):
for k in range(1):
CASEi = 'IEEE39_v33.sav'
psspy.case(CASEi)
# Convert loads (3 step process):
psspy.conl(-1,1,1)
psspy.conl(-1,1,2,[0,0],[100,0,0,100])
psspy.conl(-1,1,3)
# Convert generators:
psspy.cong()
# Solve for dynamics
psspy.ordr()
psspy.fact()
psspy.tysl()
# Save converted case
case_root = os.path.splitext(sys.argv[0])[0]
psspy.save(case_root + "_C.sav")
# Add dynamics data
#psspy.dyre_new(dyrefile="C:\Users\Desktop\\IEEE39_new\\IEEE39.dyr")
psspy.dyre_new(dyrefile="IEEE39.dyr")
# Add channels
psspy.chsb(0,1,[-1,-1,-1,1,7,1])
# Save snapshot
psspy.snap(sfile=case_root + ".snp")
#Loop through outages
for gen in GENERATORS:
study = case_root + "_SIM_%d_%s" % (gen[0],gen[1])
sys.stdout = open(study+'.log','w') # redirect all prints to this log file
# Re-load case
psspy.case(case_root + "_C.sav")
psspy.rstr(sfile=case_root + ".snp")
#psspy.dynamics_solution_params([_i,_i,_i,_i,_i,_i,_i,_i],[_f,_f, 0.02,_f,_f,_f,_f,_f],"")
psspy.dynamics_solution_params([_i,_i,_i,_i,_i,_i,_i,_i],[_f,_f,0.004,0.016,_f,_f,_f,_f],"")
# Initialize
psspy.strt(outfile=study+'.out')
psspy.run(tpause=0)
psspy.run(tpause=1)
# Disconnect generator
ierr = psspy.dist_machine_trip(gen[0],gen[1])
# Run to 60 seconds
time = 5
psspy.run(tpause=time)
#Halt
psspy.pssehalt_2()