Just after the command psspy.strt(0,out), usually there is a set of warnings that can give you a clue about what model is giving the problem
Something like this...
No active table model for Switched Shunt at bus " 3069 [JUT B438 69.000]" -- check this before continuing with the simulation FLOW1 BUS 6487 NOT FOUND--CIRCUIT T1 FROM 6487 TO 6488
Model WT3P1 Bus 3549 [CDH 0.69KV 0.6900] Machine "1 " : When WT operates at partial output, initial condition suspect may be reported for STATE(K+2). No action is needed