Juan,
In the model HYGOV, GMAX is the maximum gate limit, given as input in the dyr file as J+6
IBUS, ’HYGOV’, ID, CON(J) to CON(J+11) /
It could be that in the base case, the Pgen of the machine at bus 159 is above the Pmax, asking the model to open the gate (g, state K+2) above GMAX. As a test, try to reduce Pgen.