Unfortunately, PSSE doesn't have any channel for branch current. I see at least three alternatives for you.
Calculate from line MVA and bus voltage. Add channels with line MVA flow and bus voltage magnitude. Use a function in plotbook to calcuate I = MVA / Vpu / base voltage / 1.73205 to get the current in kA.
Use a line relay model, e.g. TIOCR1, with dummy parameters and assign the model VAR containing the line current into a channel. The line current will be in pu.