I think you should check following assumptions of your simulations:
Theoretically, RoCoF at the instant of losing a generator is calculated by the formular:
RoCoF = Delta P/(2H) with Delta P is the active power imbalance and H is the weighted inertia constant of the system.
In which H is calculated by: H = Sigma (Hi*Pi)/(sigma Pi) with Hi and Pi is inertia and power output of generator i.
Given the Hi of solar generation is zero, the increasing in penetration rate of solar will reduce the H of system and increase the RoCoF at the instant.
2 | No.2 Revision |
I think you should check following assumptions of your simulations:
Theoretically, RoCoF at the instant of losing a generator is calculated by the
formular:formula:RoCoF = f0Delta
P/(2H)P/(2Hi*Si) with Delta P is the active power imbalance andH is the weighted inertia constant of the system.In which H is calculated by: H = Sigma (Hi*Pi)/(sigma Pi) with Hi and
PiSi is inertia and apparent poweroutputrating of generator i.Given the Hi ofsolar generation is zero, theSPVs are zero. RoCoF are increase with increasingin penetration rateofsolar will reduce the H of system and increase the RoCoF at the instant.SPV penetration rate.