Check if the machine is modeled as a wind machine in the load flow case. REECA1 shall be modeled together with REEGA1. In PSSe, the test ERUN is a step voltage change.

Check if the machine is modeled as a wind machine in the load flow case. REECA1 shall be modeled together with REEGA1. In PSSe, the REGA1. PSSe has a test ERUN is named ERUN, a step voltage change.change test, but it does not work on machines defined as wind's. You can use the playback model PLBVFU1 to simulate a drop (or increase in terminal voltage at the POI of the wind plant. A sample content of the *.plb follows, 1.03 V pu is V at the POI bus before test is done:

 time,   V,   F
4.999,1.03,60
5.0  ,0.95,60
25.0 ,0.95,60