The control data are the same as in load flow. I.e. Controlled bus, vmax, vmin, step etc.

The dynamic model will change the tap position after a time delay whenever the voltage goes outside the voltage dead-band defined in load flow. First time it will take 20 s and thereafter 2.5 s/step.