1: Goto Build electrical equivalent (EEQV)

2: Define a subsystem with the buses you want to keep

3: Select button: Equivalence outside selected subssytem

4: To equivalence generators in the removed area select a high value for "Minimum generation for retaining generator buses"

5: Select Go to create the equivalent

Note:

If you select an area subsystem, area boundary buses are retained.

Area swing buses are retained. Remove therefore any "Area swing buses" lying inside the subsystem to be removed from the AREA definition before entering EEQV.