Ask Your Question

Revision history [back]

click to hide/show revision 1
initial version

A "current limiting" reactor is still a reactor, modeled in steady state with its reactance in series with the branch connected to. Start with an initial value (10% of X of branch connected to),perform a short-circuit study and move it up or down until the allowed fault MVA is achieved.