First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!

Ask Your Question

Revision history [back]

click to hide/show revision 1
initial version

answered Nov 6 '17

oppossumX gravatar image

You can use the GNET command on the machine with no dynamic parameters. This changes the machine to a negative MVA load with no dynamic response. In the GUI this is done through the "Equivalence Networks" dialog box found in the "Power Flow" menu. A GNET IDEV file can also be created and run using the runrspnsfile command.