It seems that the code updates the total load (with forecasting values). This process creates an unbalanced between generation & load, leading to progressive non-convergence since by default, the swing generator will take the delta of the MW unbalance, getting 'stressed' on higher loading. It is better to re-dispatch a group of generators after each increase in load but before a load flow solution. The re-dispatch will aim to keep all generators within their generating capabilities.
As a test, try to reach the new system load incrementally, not 'at once'
    |  2 |    No.2 Revision    |  
It seems that the code updates the total load (with forecasting values). This process creates an unbalanced between generation & load, leading to progressive non-convergence since by default, the swing generator will take the delta of the MW unbalance, getting 'stressed' on higher loading. It is better to re-dispatch a group of generators after each increase in load but before a load flow solution. The re-dispatch will aim to keep all generators within their generating capabilities.