The highlighted values below are the Max and Min governor limits in pu (on the turbine MW rating).
'GAST2A' 2 25.0 0.0 0.05 1.0 0.02 0.1 40.0 0.25 1.5 -0.1 0.01 0.77 1.0 0.05 1.0 0.4 0.0 0.2 0.8 15.0 2.5 450.0 3.3 700.0 550.0 0.23 1.3 0.5 1020.0 0.23 1020.0
Therefore, I would think that it's not possible to set them outside the range (0,1)
Try setting them as follows:
MAX = (Pmax/turbine rating)
MIN = (Pmin/turbine rating)
Note: the turbine rating to be taken in the calculation is the one entered in your dynamic model (40 MW in your case).