First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!

Ask Your Question

Revision history [back]

click to hide/show revision 1
initial version

answered Jun 1 '17

perolofl gravatar image

The turbine power in pu Mbase divided by a23 (CON(J+13)) is not within the limits specified by Pmax and Pmin (CON(J+4) and CON(J+5) respectively).

Either your dynamic data are wrongly set or the generator is overloaded in load flow!

Please specify all your data for the concerned generator!