PSS/E is based on positive sequence dynamic simulation, thus only positive sequence parameters, e.g. bus voltage could be plotted. Application of faults in dynamic simulation are limited to three-phase faults although there may be an approximation of fault impedance to emulate a line-to-ground fault.
You may try to use an EMTP-type program to do what you want since this kind of program enables unbalanced network analysis, especially transients.