Ask Your Question

Revision history [back]

click to hide/show revision 1
initial version

answered May 23 '17

EBahr gravatar image

Dynamic load models are added just like generators in .dyr file. Load models can be added by either bus, zone, area, or owner. I would take a look at section 9 of the PSSE Model Library document.

click to hide/show revision 2
No.2 Revision

Dynamic load models are added just like generators in .dyr file. Load models can be added by either bus, zone, area, or owner. I would take a look at section 9 of the PSSE Model Library document.

The following is an example of a "standard" IEEE Load Model used in the WECC:

 [AREA NUMBER] 'IEELAR' *     0.0000       1.0000       0.0000       1.0000
      0.0000       0.0000       1.0000      -1.0000       2.0000
      1.0000       0.0000       2.0000       1.0000       0.0000    /

Change [AREA NUMBER] to the area of your choice.