initial version

The negative and zero sequence are not represented in a dynamic simulation. Only the positive system is represented so it is not possible to calculate the phase voltages A, B and C for unsymmetrical fault. At simulation of unsymmetrical faults only the positive sequence voltage is calculated and plotted.