answered Apr 6 '17

perolofl gravatar image

The negative and zero sequence are not represented in a dynamic simulation. Only the positive system is represented so it is not possible to calculate the phase voltages for unsymmetrical fault. At simulation of unsymmetrical faults only the positive sequence voltage is calculated and plotted.