Perform sensitivity runs varying values for (most the) following parameters in the CMLDBU1 model: FmD – Motor D load fraction of total load Stalling voltage threshold for the residential A/C motor (Motor D) Vrst – voltage level at with restart can occur Percentage of Motor D that stalls and can recover Tth, Motor D thermal time constant, sec. Th1t, Motor D thermal protection trip start level, p.u. temperature Th2t, Motor D thermal protection trip completion level, p.u. temperature Fuvr – fraction of Motor D loads with undervoltage relay protection
2 | No.2 Revision |
Perform sensitivity runs varying values for (most the) following parameters in the CMLDBU1 model: FmD – Motor D load fraction of total load Stalling voltage threshold for the residential A/C motor (Motor D) Vrst – voltage level at with restart can occur Percentage of Motor D that stalls and can recover Tth, Motor D thermal time constant, sec. Th1t, Motor D thermal protection trip start level, p.u. temperature Th2t, Motor D thermal protection trip completion level, p.u. temperature Fuvr – fraction of Motor D loads with undervoltage relay protection
3 | No.3 Revision |
Perform sensitivity runs varying values for (most the) following parameters in the CMLDBU1 model:
model:
FmD – Motor D load fraction of total load
Stalling voltage threshold for the residential A/C motor (Motor D)
Vrst – voltage level at with restart can occur
Percentage of Motor D that stalls and can recover
Tth, Motor D thermal time constant, sec.
Th1t, Motor D thermal protection trip start level, p.u. temperature
Th2t, Motor D thermal protection trip completion level, p.u. temperature
Fuvr – fraction of Motor D loads with undervoltage relay protectionprotection
4 | No.4 Revision |
Perform sensitivity runs varying values for (most the) following parameters in the CMLDBU1 model:modelMEPPI study:
FmD – Motor D load fraction of total load
Stalling voltage threshold for the residential A/C motor (Motor D)
Vrst – voltage level at with restart can occur
Percentage of Motor D that stalls and can recover
Tth, Motor D thermal time constant, sec.
Th1t, Motor D thermal protection trip start level, p.u. temperature
Th2t, Motor D thermal protection trip completion level, p.u. temperature
Fuvr – fraction of Motor D loads with undervoltage relay protection
5 | No.5 Revision |
Perform sensitivity runs varying values for (most the) following parameters in the CMLDBU1 modelmodel (reference: MEPPI study:):
FmD – Motor D load fraction of total load
Stalling voltage threshold for the residential A/C motor (Motor D)
Vrst – voltage level at with restart can occur
Percentage of Motor D that stalls and can recover
Tth, Motor D thermal time constant, sec.
Th1t, Motor D thermal protection trip start level, p.u. temperature
Th2t, Motor D thermal protection trip completion level, p.u. temperature
Fuvr – fraction of Motor D loads with undervoltage relay protection