| 1 | initial version |
Solving this without a dummy bus is a little tricky, even PSS/E uses a dummy bus to calculate open end line faults in short circuit module!
If you still want to do it without a dummy bus you might do something like this:
Clear the fault.
The tricky thing is to calculate the fault shunt in step 3 above.
| 2 | No.2 Revision |
Solving this without a dummy bus is a little tricky, even PSS/E uses a dummy bus to calculate open end line faults in short circuit module!
If you still want to do it without a dummy bus you might do something like this:
Clear the fault.
The tricky thing is to calculate the fault shunt in step 3 above.
EDIT: Perform the simulation in the following way by using a dummy bus:
Do the following.
1: Do LTAP and place the dummy bus at From bus line end.
2: Start simulation, run to x seconds and add LG fault at Dummy bus.
3: Simulate for 6 cycles.
4: Clear fault.
5: Trip line from Dummy to From bus.
6: Apply LG fault at Dummy bus (new calculation of equivalent shunt with line open-end will be done)
6: Run for 3 cycles.
7: Disconnect Dummy bus.
8: Run to x seconds.