All your three criteria are related to machine angle. For simplicity I prefer the first.
Instability of the system is about how the remaining system performs post-fault conditions, subject to all tripping activated by the protection system. Does it reach a stable condition (in V, F) at the end of the simulation? Good and sufficient modeling is needed for this kind of assessment.
For a test event, system instabilty can be monitored by:
angle of generators, relative to reference machine like a nuclear plant or base unit. [generic model available in PSSe] Realistic criteria for the protection relays is needed (why trip a unit when its relative angle is 100 deg and not at 120 deg.?) Tripping of a unit might not render a system unstable.
buses voltage level leading to voltage collapse or high-voltage cascading. Add UVLS relays [generic v-monitoring model available in PSSe, also UV/OV relays] Add load dynamic model reflecting V & F dependance. Air-conditioner loads?
undamped oscillation, is damping > 3%?. Use Prony analysis after filtering visually all plots.
CCT studies help to set the initial protection of generators for angle separation but not needed to asses the stability of a system. Dynamic stability studies take time, need running multiple scenarios under many fault tests. I recommend driving PSSe in parallel processing for that.
2 | No.2 Revision |
All your three criteria are related to machine angle. For simplicity I prefer the first.
Instability of the system is about how the remaining system performs post-fault conditions, subject to all tripping activated by the protection system. Does it reach a stable condition (in V, F) at the end of the simulation? Good and sufficient modeling is needed for this kind of assessment.
For a test event, system instabilty can be monitored by:
angle of generators, relative to reference machine like a nuclear plant or base unit. [generic model available in PSSe] Realistic criteria for the protection relays is needed (why trip a unit when its relative angle is 100 deg and not at 120 deg.?) Tripping of a unit might not render a system unstable.
buses voltage level leading to voltage collapse or high-voltage cascading. Add UVLS relays [generic v-monitoring model available in PSSe, also UV/OV relays] Add load dynamic model reflecting V & F dependance. Air-conditioner loads?
undamped oscillation, is damping > 3%?. Use Prony analysis after filtering visually all plots.
CCT studies help to set the initial protection of generators for angle separation but not needed to asses assess the stability of a system. Dynamic stability studies take time, need running multiple scenarios under many fault tests. I recommend driving PSSe in parallel processing for that.