Some ideas: 1- Set all generation to control their own bus. 2- the swing generator (bus 1) was not a true 'infinite' machine. Better use a classical model, with no excitation model. 3- PV units have limited Pmax and Qmax, Qmin. I set 1.5 MW and +/- 0.5 Mvar. 4- Load needs to be converted before running a dynamic simulation.