You can have different breaker values. The trick is to separate the UV relay definition from the OV by using more than one relay record. The example below is for a VRT relay schema.

/MINS model     M     M+1 M+2  VL   VU    TP    TB  /
1     'VTGTPAT' XXXX  xxx xx   -1   1.3   0.034 0.1 /
2     'VTGTPAT' XXXX  xxx xx   -1   1.2   0.5   0.1 / 
3     'VTGTPAT' XXXX  xxx xx   -1   1.1   5     0.1 / 
4     'VTGTPAT' XXXX  xxx xx  0.1   5     0.15  0.12 / 
5     'VTGTPAT' XXXX  xxx xx  0.9   5     3     0.12 /