First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
| 1 | initial version |
If I were you, I would first take all the N-1 line outages in powerflow and make sure they are good to go (ie; solve correctly and not blown up), then save them as individual cases and put them all in the same folder. Then create some code similar to this: https://psspy.org/psse-help-forum/question/1118/dynamic-simulations-using-python/, but wrap most of it up in a for loop that changes the case each loop. ie;
import os,sys
import glob
import psspy
import redirect
PYTHONPATH = r'C:\Program Files (x86)\PTI\PSSE32\PSSBIN'
sys.path.append(PYTHONPATH)
os.environ['PATH'] += ';' + PYTHONPATH
#Modify GENERATORS to include generators you want to trip in form of [[BUS #, 'GEN_ID'],[BUS #, 'GEN_ID']....]
GENERATORS = [[32,'1'],[35,'1'],[37,'1'],[38,'1'],[39,'1']] #GEN_ID might not be correct here...
# Redirect output from PSSE to Python:
redirect.psse2py()
# Loop through cases
for CASE in glob.glob(os.path.join('C:\\YOUR\\DIRECTORY\\', '*.sav')):
psspy.psseinit(12000)
psspy.case(CASE)
# Convert loads (3 step process):
psspy.conl(-1,1,1)
psspy.conl(-1,1,2,[0,0],[100,0,0,100])
psspy.conl(-1,1,3)
# Convert generators:
psspy.cong()
# Solve for dynamics
psspy.ordr()
psspy.fact()
psspy.tysl()
# Save converted case
case_root = os.path.splitext(sys.argv[1])[0]
psspy.save(case_root + "_C.sav")
# Add dynamics data
psspy.dyre_new(dyrefile="C:\\YOUR\\DIRECTORY\\YOUR_DYRE.DYR")
# Add channels
#ADD CHANNEL CODE HERE IF YOU NEED IT
# Save snapshot
psspy.snap(sfile=case_root + ".snp")
#Loop through outages
for gen in GENERATORS:
# Re-load case
psspy.open(case_root + "_C.sav")
psspy.rstr(sfile=case_root + ".snp")
# Initialize
psspy.strt(outfile=case_root + "_SIM_%d_%s.out" % (gen[0],gen[1]))
psspy.run(tpause=0)
# Disconnect generator
ierr = dist_machine_trip(gen[0],gen[1])
# Run to 20 seconds
time = 20
psspy.run(tpause=time)
# Halt
psspy.pssehalt_2()
I haven't tested that code, but it should hopefully be something close to what you are looking for.