You can use the models REGCA1, REECA1 and REPCA1. For example, in the Argentina power system model maintained by CAMMESA the generic renewable model for wind farm is as follows:
622 'REGCA1' 2 0
0.20000E-01 10.000 1.0000 0.0000 1.0000
1.2000 0.78000 0.30000 -1.0500 0.0000
0.0000 999.00 -999.00 1.0000 /
622 'REECA1' 2
0 0 1 0 0 0
0.90000 1.1000 0.0000 -0.10000 0.10000
2.0000 1.0500 -1.0500 1.0000 0.0000
0.0000 0.0000 0.50000E-01 0.67000 -0.67000
1.2000 0.80000 5.0000 10.000 1.0000
50.000 0.10000 0.0000 99.000 -99.000
1.0000 0.0000 1.7000 0.40000E-01 0.10000E-01
1.1000 1.2000 1.1000 0.0000 0.0000
0.0000 0.0000 0.0000 1.1500 1.1000
1.2400 2.0000 1.2400 0.0000 0.0000 /
622 'REPCA1' 2
622 622 577 '2 ' 0 1 1
0.10000E-01 0.0000 1.7500 0.0000 0.0000
0.90000 0.0000 0.0000 0.0000 9999.0
-9999.0 0.0000 0.0000 1.0000 -1.0000
0.0000 1.5000 0.25000 -0.80000E-02 0.80000E-02
0.12000E-01 -0.12000E-01 1.0000 0.0000 0.0000
8.3300 0.0000 /
For the PV plants allmost all parameters reamins constants except a few in the REPCA1 model.
5610 'REGCA1' 1 0
0.20000E-01 10.000 1.0000 0.0000 1.0000
1.2000 0.78000 0.30000 -1.0500 0.0000
0.0000 999.00 -999.00 1.0000 /
5610 'REECA1' 1
0 0 1 0 0 0
0.90000 1.1000 0.0000 -0.10000 0.10000
2.0000 1.0500 -1.0500 1.0000 0.0000
0.0000 0.0000 0.50000E-01 0.67000 -0.67000
1.2000 0.80000 5.0000 10.000 1.0000
50.000 0.10000 0.0000 99.000 -99.000
1.0000 0.0000 1.7000 0.40000E-01 0.10000E-01
1.1000 1.2000 1.1000 0.0000 0.0000
0.0000 0.0000 0.0000 1.1500 1.1000
1.2400 2.0000 1.2400 0.0000 0.0000 /
5610 'REPCA1' 1
5610 5610 5555 '1 ' 0 1 1
0.10000E-01 20.000 10.000 0.0000 1.5000
0.40000E-01 0.0000 0.0000 0.0000 9999.0
-9999.0 0.0000 0.0000 1.0000 -1.0000
0.50000E-01 0.55000 0.25000 -0.80000E-02 1.0000
9999.0 -9999.0 1.0000 0.0000 0.30000
6.1000 0.0000 /