Clear fault just removes the fault shunt inserted by distbranchfault.
Branch faults are modelled with a large line shunt on the faulted line. Tripping the line, means that the fault is isolated from the rest of the system, i.e. the fault is cleared at time 1.05 when the line is tripped.
![]() | 2 | No.2 Revision |
Clear fault just removes the fault shunt inserted by distbranchfault.dist_branch_fault
.
Branch faults are modelled with a large line shunt on the faulted line. Tripping the line, means that the fault is isolated from the rest of the system, i.e. the fault is cleared at time 1.05 when the line is tripped.