![]() | 1 | initial version |
For reference, search the forum for "initial condition suspect". If the network and dyr data does not change, multiple STRT would not be different from the first STRT outcome. Having state variables not OK, one trick is to run dynamics for x-seconds and test the outfile for max. deviations. Keep/save the case and snap file for the scenario with acceptable low deviations.
A better approach is to resolve the states that are listed in the "initial condition suspect" table inside the log following the STRT activity. exa.: if the "initial condition suspect" table list a state var belonging to a governor model, check if the corresponding generator in the load flow may need to adjust its power output or a dyr value in the governor model can be tuned/revised/changed.