1 | initial version |
Here are two examples of what is printed while the robust solver runs.
Example for case 1:
Processing contingency "SING OPN LIN 75 558-1529(1)" (#75 of 862):
OPEN LINE FROM BUS 558 NAME1 380.00] TO BUS 1529 [NAME2 380.00] CKT 1
Successful solution not achieved: Iteration limit exceeded
Largest mismatch is 113.04 MW or Mvar at bus 160396 [NAME3 330.00]
Total mismatch is 432.00 MVA
Storing the original solution state and options...
Attempting to solve with original settings...
Attempting to solve with various solution methods...
Attempting to solve with Data Check...
Attempting to solve with Var limit option change...
Attempting to solve with Constant Y load when load bus voltage is below PQBRAK...
Attempting to solve with low acceleration and high iterations...
Maximum mismatch changed from 90.86 MVA to 58.69 MVA at bus 160396.
Attempting to solve with more options...
Maximum mismatch changed from 58.69 MVA to 2.53 MVA at bus 160504.
Attempting to solve with Locking small generators...
Attempting to solve with locking 1391 generators with var band smaller than 4.00...
Solution failed. Restoring case and settings to ORIGINAL state.
Robust power flow solution UNSUCCESSFUL.
Testing RAS conditions after application of contingency [SING OPN LIN 75 558-1529(1)]
Example for case 2:
Processing contingency "SING OPN TIE 240 2786-20234(1)" (#240 of 697):
OPEN LINE FROM BUS 2786 [NAME1 380.00] TO BUS 20234 [NAME2 380.00] CKT 1
Testing RAS conditions after application of contingency [SING OPN TIE 240 2786-20234(1)]
Implemented action for RAS: [SPS1]
Warning: Bus 1223 [NAME3 220.00] is a type 3 bus with no plant or machine data
Successful solution not achieved: Iteration limit exceeded
Largest mismatch is 18.53 MW or Mvar at bus 1223 [NAME3 220.00]
Total mismatch is 76.24 MVA
Storing the original solution state and options...
Attempting to solve with original settings...
Maximum mismatch changed from 18.72 MVA to 18.72 MVA at bus 1221.
Robust power flow solution SUCCESSFUL, but control option adjustments required!
RAS Iteration 2:
RAS Condition Check All Clear
2 | No.2 Revision |
Here are two examples of what is printed while the robust solver runs.
Example for case 1:
Processing contingency "SING OPN LIN 75 558-1529(1)" (#75 of 862):
OPEN LINE FROM BUS 558 NAME1 380.00] TO BUS 1529 [NAME2 380.00] CKT 1
Successful solution not achieved: Iteration limit exceeded
Largest mismatch is 113.04 MW or Mvar at bus 160396 [NAME3 330.00]
Total mismatch is 432.00 MVA
Storing the original solution state and options...
Attempting to solve with original settings...
Attempting to solve with various solution methods...
Attempting to solve with Data Check...
Attempting to solve with Var limit option change...
Attempting to solve with Constant Y load when load bus voltage is below PQBRAK...
Attempting to solve with low acceleration and high iterations...
Maximum mismatch changed from 90.86 MVA to 58.69 MVA at bus 160396.
Attempting to solve with more options...
Maximum mismatch changed from 58.69 MVA to 2.53 MVA at bus 160504.
Attempting to solve with Locking small generators...
Attempting to solve with locking 1391 generators with var band smaller than 4.00...
Solution failed. Restoring case and settings to ORIGINAL state.
Robust power flow solution UNSUCCESSFUL.
Testing RAS conditions after application of contingency [SING OPN LIN 75 558-1529(1)]
Example for case 2:
Processing contingency "SING OPN TIE 240 2786-20234(1)" (#240 of 697):
OPEN LINE FROM BUS 2786 [NAME1 380.00] TO BUS 20234 [NAME2 380.00] CKT 1
Testing RAS conditions after application of contingency [SING OPN TIE 240 2786-20234(1)]
Implemented action for RAS: [SPS1]
Warning: Bus 1223 [NAME3 220.00] is a type 3 bus with no plant or machine data
Successful solution not achieved: Iteration limit exceeded
Largest mismatch is 18.53 MW or Mvar at bus 1223 [NAME3 220.00]
Total mismatch is 76.24 MVA
Storing the original solution state and options...
Attempting to solve with original settings...
Maximum mismatch changed from 18.72 MVA to 18.72 MVA at bus 1221.
Robust power flow solution SUCCESSFUL, but control option adjustments required!
RAS Iteration 2:
RAS Condition Check All Clear
3 | No.3 Revision |
Here are two examples is an example of what is printed while the robust solver runs.
Example for case 1:
Processing contingency "SING OPN LIN 75 558-1529(1)" (#75 of 862):
OPEN LINE FROM BUS 558 NAME1 380.00] TO BUS 1529 [NAME2 380.00] CKT 1
Successful solution not achieved: Iteration limit exceeded
Largest mismatch is 113.04 MW or Mvar at bus 160396 [NAME3 330.00]
Total mismatch is 432.00 MVA
Storing the original solution state and options...
Attempting to solve with original settings...
Attempting to solve with various solution methods...
Attempting to solve with Data Check...
Attempting to solve with Var limit option change...
Attempting to solve with Constant Y load when load bus voltage is below PQBRAK...
Attempting to solve with low acceleration and high iterations...
Maximum mismatch changed from 90.86 MVA to 58.69 MVA at bus 160396.
Attempting to solve with more options...
Maximum mismatch changed from 58.69 MVA to 2.53 MVA at bus 160504.
Attempting to solve with Locking small generators...
Attempting to solve with locking 1391 generators with var band smaller than 4.00...
Solution failed. Restoring case and settings to ORIGINAL state.
Robust power flow solution UNSUCCESSFUL.
Testing RAS conditions after application of contingency [SING OPN LIN 75 558-1529(1)]