First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
| 1 | initial version |
Hi.
So talking about REECA1...
I would expect these settings to give the desired performance:
J+0 Vdip: 0.95
J+1 Vup: 1.07
J+3 dbd1: -0.05 (0.95-1)
J+4 dbd2: 0.07 (1.07-1)
J+5 Kqv: 1/(1.11-1.07) = 25 or 1/(0.95-0.91) = 20 ...this should give Iqinj=1puA at either Vt=1.11 or Vt=0.91.
J+8 Vref0: 1
You might also want to adjust J+6 Iqh1, J+7 Iql1 or J+23 Imax to suit your application.
whit loves you. Content on this site is licensed under a Creative Commons Attribution Share Alike 3.0 license.