| 1 | initial version |
Select Subsystem Power Total for All Buses. This will add five channels with total PMECH, PELEC, PACCEL, PLOAD and PE-PL for all generators. Channel PMECH FOR ALL BUSES shows the the total turbine power in MW.
An example with trip og generator 3018 in savnw network:

After trip of generator 3018 the total PMECH is 3185.7 MW. At the new steady state the turbine power is 3266.4 MW. The total governor response is 3266.4-3185.7 = 80.7 MW.