First, make sure the Q output is set to zero in load flow.
You can set the activation thresholds to very 'wide' values so that Fault Ride Through Mode isn't entered. E.g set REECCU1 J+0 to 0 [puV] and J+1 to 2 [puV]. There are probably some other settings to change as well...refer to the MODELS entry in the manual.
Also, if you don't want reactive current injection, what do you expect the dynamic model to do, and why are you using a dynamic model? You could just use a negative load with MW only. The post-fault MW recovery profile would be greatly simplified, but the setup would be very easy.