The model will trip a selected line whenever the rate of change of the active power on the monitored line (IBUS, JBUS, ID) is larger than X MW/s during a given number of time steps. The power must also be larger than the threshold given in CON(J+3).

It is up to you to select a proper value for your application. Enter a small value to disable the derivative criterion and only use the power limit criterion for tripping.