1 | initial version |
In order to get a load flow case with the P and Q flow between two busses at a particular level, do an iterative process: - run load flow - measure P and Q flow - adjust P and Q for the generator
here is some sample code:
def dispatchpandpf(psetpoint, pfsetpoint, pgenbus, qgenbus, Qfrombus, Qtobus, Pfrombus, Ptobus):
# itteratively adjusts two machines in the load flow case, until the P and Q flows between the measbus and pocbus match the setpoints.
# The machines at which P and Q are afjusted are allowed to be different, for cases where P is set by a genertor and Q by a STATCOM
psched = psetpoint
qsched = defaultpsp sqrt((1/pf_setpoint)*2 - 1) * np.sign(pfsetpoint)
count = 0
pgen = psched
qgen = qsched
print('Perror \tQerror \tPctrl \tQctrl \tPgen \tQgen' )
while count < nbrsolveiterations:
psspy.machinechng2(pgenbus,r"""1""",[i,i,i,i,i,i],[ pgen,f,f,f,f,f,f,f,f,f,f,f,f,f,f,f])
psspy.machinechng2(qgenbus,r"""1""",[i,i,i,i,i,i],[ _f,qgen,qgen,qgen,f,f,f,f,f,f,f,f,f,f,f,f])
psspy.fdns([0,2,0,0,0,0,99,0])
psspy.fdns([0,2,0,0,0,0,99,0])
ierr, pcontrol = psspy.brnmsc(Pfrombus, Ptobus, '1','P')
ierr, qcontrol = psspy.brnmsc(Qfrombus, Qtobus, '1','Q')
perror = psched - pcontrol
qerror = qsched - qcontrol
if abs(perror) < errortol and abs(qerror) < errortol :
break # the systesm is now set up correctly
pgen = pgen + perror
if pgen > Pbase:
pgen = Pbase
qgen = qgen + qerror
count +=1
print('%3.2f \t%3.2f \t%3.2f \t%3.2f \t%3.2f \t%3.2f' % (p_error, q_error, p_control, q_control, p_gen, q_gen))
2 | No.2 Revision |
In order to get a load flow case with the P and Q flow between two busses at a particular level, do an iterative process: - run load flow - measure P and Q flow - adjust P and Q for the generator
here is some sample code:
code:
def dispatchpandpf(psetpoint, pfsetpoint, pgenbus, qgenbus, Qfrombus, Qtobus, Pfrombus, Ptobus):
dispatch_p_and_pf(p_setpoint, pf_setpoint, p_gen_bus, q_gen_bus, Q_from_bus, Q_to_bus, P_from_bus, P_to_bus):
# itteratively iteratively adjusts two machines in the load flow case, until the P and Q flows between the measbus and pocbus meas_bus and poc_bus match the setpoints.
# The machines at which P and Q are afjusted adjusted are allowed to be different, for cases where P is set by a genertor generator and Q by a STATCOM
psched = psetpoint
qsched = defaultpsp sqrt((1/pf_setpoint)*2 p_sched = p_setpoint
q_sched = default_p_sp *sqrt((1/pf_setpoint)**2 - 1) * np.sign(pfsetpoint)
np.sign(pf_setpoint)
count = 0
pgen = psched
qgen = qsched
p_gen = p_sched
q_gen = q_sched
print('Perror \tQerror \tPctrl \tQctrl \tPgen \tQgen' )
while count < nbrsolveiterations:
psspy.machinechng2(pgenbus,r"""1""",[i,i,i,i,i,i],[ pgen,f,f,f,f,f,f,f,f,f,f,f,f,f,f,f])
psspy.machinechng2(qgenbus,r"""1""",[i,i,i,i,i,i],[ _f,qgen,qgen,qgen,f,f,f,f,f,f,f,f,f,f,f,f])
nbr_solve_iterations:
psspy.machine_chng_2(p_gen_bus,r"""1""",[_i,_i,_i,_i,_i,_i],[ p_gen,_f,_f,_f,_f,_f,_f,_f,_f,_f,_f,_f,_f,_f,_f,_f])
psspy.machine_chng_2(q_gen_bus,r"""1""",[_i,_i,_i,_i,_i,_i],[ _f,q_gen,q_gen,q_gen,_f,_f,_f,_f,_f,_f,_f,_f,_f,_f,_f,_f])
psspy.fdns([0,2,0,0,0,0,99,0])
psspy.fdns([0,2,0,0,0,0,99,0])
ierr, pcontrol = psspy.brnmsc(Pfrombus, Ptobus, p_control = psspy.brnmsc(P_from_bus, P_to_bus, '1','P')
ierr, qcontrol = psspy.brnmsc(Qfrombus, Qtobus, q_control = psspy.brnmsc(Q_from_bus, Q_to_bus, '1','Q')
perror = psched - pcontrol
qerror = qsched - qcontrol
p_error = p_sched - p_control
q_error = q_sched - q_control
if abs(perror) abs(p_error) < errortol and abs(qerror) error_tol and abs(q_error) < errortol error_tol :
break # the systesm is now set up correctly
pgen = pgen p_gen = p_gen + perror
p_error
if pgen p_gen > Pbase:
pgen p_gen = Pbase
qgen = qgen
q_gen = q_gen + qerror
q_error
count +=1
print('%3.2f \t%3.2f \t%3.2f \t%3.2f \t%3.2f \t%3.2f' % (p_error, q_error, p_control, q_control, p_gen, q_gen))