To maintain a flow below a level: - Change the dispatch of nearby generation according to their generation shift factor relative to the branch whenever the branch flow is closed to reach its limit.

On higher power levels (Pflow > 50 MW), to maintain a fix flow on a branch: - Add a phase-shifter transformer in series with the branch. or - Add a HVDC line in series with the branch.