Yes, you can use hreewndwindingdata3. For example, to change ratio for winding 1 to 1.01667:
psspy.three_wnd_winding_data_3(ibus2, jbus, kbus, ickt,1, realari1= 1.01667)
The fifth argument is the winding number; 1, 2 or 3.
The unit for the ratio is determined by code CW. It may be in per unit on bus base voltage, winding voltage in kV or per unit on winding nominal voltage.