Before the dynamic run is executed, for all loads with CMLDBLDGU2 model in the dyr file (v.34 or v.35), confirm that in the case, load table, the columns "Distributed Gen (MW)", "Distributed Gen (MVAR)" have values and "Distributed Gen Mode" is set to 'On'.
Also after the run, check the log file for error messages saying that model CMLDBLDGU2 was not assigned/ignored.